Karl Townsend  
View profile
 More options Jul 5, 8:10 pm
Newsgroups: rec.crafts.metalworking
From: "Karl Townsend" <karltownsend....@embarqmail.com>
Date: Sat, 5 Jul 2008 19:10:46 -0500
Local: Sat, Jul 5 2008 8:10 pm
Subject: pressure switch wire
My well is located 400+ feet from the storage tanks and pressure switch in
the basement. I buried a 12-2 romex with the pipe 22 years ago. This spring
one of the wires shorted so I made a bastard hookup up using the ground and
the remaining good wire. Today the second one shorted, so I made a double
bastard - hot from power in house to one of the wires and cut the other two
loose. Pick up a ground at the well.  Works for today, need to put on high
priority to repair.

Using underground romex again will push $150. Wire has gotten spendy. I see
underground irrigation cable in McMaster Carr #8045k11 that's rated for 30
volt. My question, would a 24 VAC supply in the basement powering  24 volt
relay at the well contactor be a reliable setup? As in last 20 years? This
would save $ on wire and I wouldn't have to bury it more than 6 inches deep.

other ideas?


    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
Bob AZ  
View profile
 More options Jul 5, 8:24 pm
Newsgroups: rec.crafts.metalworking
From: Bob AZ <rwatson...@aol.com>
Date: Sat, 5 Jul 2008 17:24:58 -0700 (PDT)
Local: Sat, Jul 5 2008 8:24 pm
Subject: Re: pressure switch wire

> other ideas?

Karl

You can find the cable/wire on Ebay for less than 150. And use water
pipe for conduit. But all this is not to code so beware the code
inspectors if this is a problem.


    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
Paul  
View profile
 More options Jul 5, 8:33 pm
Newsgroups: rec.crafts.metalworking
From: "Paul" <pl...@budweiser.com>
Date: Sat, 5 Jul 2008 17:33:30 -0700
Local: Sat, Jul 5 2008 8:33 pm
Subject: Re: pressure switch wire

"Karl Townsend" <karltownsend....@embarqmail.com> wrote in message

news:48700df9$0$2557$892e0abb@auth.newsreader.octanews.com...

I'm puzzled. How are you planning to get power to the pump (110v or 220v)
from the house to the well. I'm assuming you are dealing with a submersible
pump in the well. Maybe a little more info would help.
Paul

    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
Karl Townsend  
View profile
 More options Jul 5, 8:51 pm
Newsgroups: rec.crafts.metalworking
From: "Karl Townsend" <karltownsend....@embarqmail.com>
Date: Sat, 5 Jul 2008 19:51:54 -0500
Local: Sat, Jul 5 2008 8:51 pm
Subject: Re: pressure switch wire

> I'm puzzled. How are you planning to get power to the pump (110v or 220v)
> from the house to the well. I'm assuming you are dealing with a
> submersible pump in the well. Maybe a little more info would help.

Power goes out on #4 underground direct from the meter. This is just the
signal from the pressure switch to the motor contactor

karl


    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
Vaughn Simon  
View profile
 More options Jul 5, 10:05 pm
Newsgroups: rec.crafts.metalworking
From: "Vaughn Simon" <vaughnsimonHATESS...@att.FAKE.net>
Date: Sun, 06 Jul 2008 02:05:50 GMT
Local: Sat, Jul 5 2008 10:05 pm
Subject: Re: pressure switch wire

"Karl Townsend" <karltownsend....@embarqmail.com> wrote in message

news:48700df9$0$2557$892e0abb@auth.newsreader.octanews.com...

> Using underground romex again will push $150. Wire has gotten spendy. I see
> underground irrigation cable in McMaster Carr #8045k11 that's rated for 30
> volt. My question, would a 24 VAC supply in the basement powering  24 volt
> relay at the well contactor be a reliable setup? As in last 20 years? This
> would save $ on wire and I wouldn't have to bury it more than 6 inches deep.

   I read your explanation downthread that this is only a control line.  I
believe that your idea will work, but I would feel more secure installing 1/2"
minimum conduit so that you can easily fix any future problems, and then use
ordinary THHN conductors.  Sorry, I haven't saved you any money, but you have
discovered why I don't dirrect bury electrical cable.  Conduit can be expensive,
but it is cheap compared to the price/labor of digging a new ditch.


    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
Pete C.  
View profile
 More options Jul 5, 10:20 pm
Newsgroups: rec.crafts.metalworking
From: "Pete C." <aux3.DO...@snet.net>
Date: Sat, 05 Jul 2008 21:20:07 -0500
Local: Sat, Jul 5 2008 10:20 pm
Subject: Re: pressure switch wire

I'm missing that as well.

For all things underground, the answer is *always* conduit. Run
appropriately sized PVC conduit, I'd probably say 1" would do, and pull
individual THHN conductors through it.

If you have power at the well head from some other source, then just a
low voltage control signal would work, or you could relocate the
pressure switch to the well house.


    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
Karl Townsend  
View profile
 More options Jul 5, 10:40 pm
Newsgroups: rec.crafts.metalworking
From: "Karl Townsend" <karltownsend....@embarqmail.com>
Date: Sat, 5 Jul 2008 21:40:43 -0500
Local: Sat, Jul 5 2008 10:40 pm
Subject: Re: pressure switch wire

>   I read your explanation downthread that this is only a control line.  I
> believe that your idea will work, but I would feel more secure installing
> 1/2" minimum conduit so that you can easily fix any future problems, and
> then use ordinary THHN conductors.  Sorry, I haven't saved you any money,
> but you have

Well, I already have a stock of THHN wire from an auction. And a large
supply of 1/2 PVC pipe. So this route would be VERY cheap. Now, that conduit
will eventually fill with water (all underground runs will). I'm surprised
THHN would be rated for years of water and ice exposure. Is this true????

Karl


    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
Paul  
View profile
 More options Jul 5, 10:44 pm
Newsgroups: rec.crafts.metalworking
From: "Paul" <pl...@budweiser.com>
Date: Sat, 5 Jul 2008 19:44:42 -0700
Local: Sat, Jul 5 2008 10:44 pm
Subject: Re: pressure switch wire

"Karl Townsend" <karltownsend....@embarqmail.com> wrote in message

news:4870179c$0$2555$892e0abb@auth.newsreader.octanews.com...

>> I'm puzzled. How are you planning to get power to the pump (110v or 220v)
>> from the house to the well. I'm assuming you are dealing with a
>> submersible pump in the well. Maybe a little more info would help.

> Power goes out on #4 underground direct from the meter. This is just the
> signal from the pressure switch to the motor contactor

> karl

OK, I get it now. Your idea would work, but it might be easier and simpler
to move the pressure switch from the house to the well. The pressure switch
really doesn't care where in the system that it's located, as long as it can
sense the pressure.
In the future, when running electricity underground, ALWAYS use conduit
(grey PVC), then pull THWN wire through it. If you ever have a problem with
the wire, it's a simple matter to replace it.
Paul

    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
Karl Townsend  
View profile
 More options Jul 5, 11:12 pm
Newsgroups: rec.crafts.metalworking
From: "Karl Townsend" <karltownsend....@embarqmail.com>
Date: Sat, 5 Jul 2008 22:12:09 -0500
Local: Sat, Jul 5 2008 11:12 pm
Subject: Re: pressure switch wire

> OK, I get it now. Your idea would work, but it might be easier and simpler
> to move the pressure switch from the house to the well. The pressure
> switch really doesn't care where in the system that it's located, as long
> as it can sense the pressure.

NOT true. I tried it. There is a pressure wave that will kick out a pressure
switch when the pump first comes on. Then the pressure drops right off and
the switch closes. result is pump rapidly cycles on/off/on/off.

> In the future, when running electricity underground, ALWAYS use conduit
> (grey PVC), then pull THWN wire through it. If you ever have a problem
> with the wire, it's a simple matter to replace it.
> Paul

I've not heard of THWN and I'm not seeing it listed in Mcmaster or grainger.
Tell me more about it and where to purchase.

Karl


    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
RoyJ  
View profile
 More options Jul 5, 11:15 pm
Newsgroups: rec.crafts.metalworking
From: RoyJ <spaml...@microsoft.net>
Date: Sat, 05 Jul 2008 22:15:05 -0500
Local: Sat, Jul 5 2008 11:15 pm
Subject: Re: pressure switch wire
If you have power out at the well, why have 800' of wire for voltage
loss? Run some low voltage control circuits out there.

As the others have said: use PVC conduit so you can replace wire as
required. Actually, you really want to drop in TWO conduits so you can
run power in one and control in the other.


    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
Pete C.  
View profile
 More options Jul 5, 11:27 pm
Newsgroups: rec.crafts.metalworking
From: "Pete C." <aux3.DO...@snet.net>
Date: Sat, 05 Jul 2008 22:27:33 -0500
Local: Sat, Jul 5 2008 11:27 pm
Subject: Re: pressure switch wire

Karl Townsend wrote:

> > OK, I get it now. Your idea would work, but it might be easier and simpler
> > to move the pressure switch from the house to the well. The pressure
> > switch really doesn't care where in the system that it's located, as long
> > as it can sense the pressure.

> NOT true. I tried it. There is a pressure wave that will kick out a pressure
> switch when the pump first comes on. Then the pressure drops right off and
> the switch closes. result is pump rapidly cycles on/off/on/off.

You need a buffer / accumulator tank and/or flow restrictor to the
pressure switch then.

> > In the future, when running electricity underground, ALWAYS use conduit
> > (grey PVC), then pull THWN wire through it. If you ever have a problem
> > with the wire, it's a simple matter to replace it.
> > Paul

> I've not heard of THWN and I'm not seeing it listed in Mcmaster or grainger.
> Tell me more about it and where to purchase.

Check your THHN markings, you'll in all probability find it has a
multiple listing including THWN.